New AFCI Breaker Tripping

I had a few new AFCI breakers just installed in our basement. One of the new 20-amp circuits keeps tripping. I can plug a night light or a small LED strand of Christmas lights into an outlet on the circuit, and it doesn't trip. If I plug in a power tool battery charger or vacuum cleaner, it trips immediately. I just went through the ritual of opening every outlet cover to make sure none of the wiring came loose, but it all looks good. Is this likely just to be a faulty new breaker? What would be my next troubleshooting steps?
 
Sponsored Links
  #2  
Old 12-28-19, 10:58 AM
C
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 69
Received 1 Vote on 1 Post
I have been reading about incompatibility issues between certain electrical devices. I have a second identical AFCI breaker just installed on a different circuit at the same time. The vacuum cleaner and battery charger do not trip that circuit.
 
  #3  
Old 12-28-19, 11:01 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,638
Received 1,167 Votes on 1,082 Posts
If they are the same size breaker....... swap them. It can be a defective breaker.
 
  #4  
Old 12-28-19, 07:00 PM
L
Member
Join Date: Sep 2019
Posts: 41
Received 9 Votes on 6 Posts
Might be a neutral-ground short. A GFCI breaker would trip without any load, but with AFCIs (except GE), only with some load.
 
  #5  
Old 12-29-19, 05:15 AM
A
Member
Join Date: Mar 2014
Posts: 560
Received 17 Votes on 17 Posts
The first thing to do is what PJMax suggested. Since you had several AFCI breakers installed try using one of the other ones on the same circuit that is tripping the said AFCI breaker. If it does not trip under the same exact scenario then the said breaker may be faulty. If after you swap with another AFCI breaker that breaker trips under the same exact scenario then the problem is in the circuit.

Do this test of swapping and then report back the findings and then we can take it from there; otherwise it is all just guess work.

NOTE: before you perform this swapping, do you feel comfortable enough to work in a live panel? Have you worked in a live panel in the past? Do you have a disconnect prior to this panel that will allow you to disconnect the power to this panel before swapping the breaker? We just don't know your skill level yet.

Also GFCI breaker is not playing any role in this issue that we know of. It was reported by the OP that the breakers are AFCI breakers.
 
  #6  
Old 12-30-19, 06:24 AM
C
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 69
Received 1 Vote on 1 Post
Thanks for all of the feedback, guys. I eventually figured out that it was a faulty outlet.

Shortly after posting my question, I decided to try picking an outlet about halfway down the circuit, disconnecting the circuit at that point, then turning the power back on and plugging devices into the hot half of the circuit. It didn't trip. So I kept working my way down the circuit, reconnecting/disconnecting one outlet at a time, until I finally got it to trip again. I then replaced that outlet, and now all is well.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: