EMT conduit fill

I've read conflicting information. When you read the maximum number of conductors in an EMT conduit - does that typically include the ground wire? Obviously it takes up physical space but do those allowable numbers include it or not?
 
  #2  
Old 02-24-23, 09:00 AM
T
Member
Join Date: Sep 2015
Location: US
Posts: 1,237
Received 209 Upvotes on 183 Posts
You may be confusing box fill and conduit fill. Yes, each individual ground conductor counts toward conduit fill. And it's not just the number of conductors, its also their size. and if there are different size conductors in the pull, don't use the tables, do the math instead.
 
  #3  
Old 02-24-23, 11:57 AM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 560
Received 2 Upvotes on 2 Posts
Actually I wasn't mixing the two up. I've seen information saying a ground wire does not count toward conduit fill. I would think it should simply from the physical space it occupies.
 
  #4  
Old 02-24-23, 12:57 PM
T
Member
Join Date: Sep 2015
Location: US
Posts: 1,237
Received 209 Upvotes on 183 Posts
When 3 or more conductors are placed in a conduit. the sum of the outer diameters of all conductors (based on size and insulation) cannot exceed 40% of the inner diameter of the conduit.

Then you have to pull them in. Pulling force depends on a lot of things like, length of pull, type of raceway (conduit), conductor insulation type, number and degree of bends, etc.
 
  #5  
Old 02-24-23, 01:25 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,428
Received 900 Upvotes on 761 Posts
The ground wire counts for conduit fill but it does not count for ampacity adjustments required when you have more than 3 current carrying conductors in a raceway.
 
 