Smoke detector audible requirement


  #1  
Old 02-17-17, 06:21 PM
T
Member
Thread Starter
Join Date: Mar 2010
Location: usa
Posts: 610
Likes: 0
Received 0 Likes on 0 Posts
Smoke detector audible requirement

AHJ's require all smokes to sound during an alarm, not just one.

Does anyone know how to get a Vista20 to comply?

Whether it is through 2-wire or 4-wire smokes [preferably 4-wire]..
 
  #2  
Old 02-17-17, 07:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,925
Received 3,162 Likes on 2,841 Posts
It's not the Vista that is the problem..... it's the wiring.
Two wires for the detector and two for the audible.

This explains it pretty well. system sensor/i3-Series_DataSheet_A05-0348.pdf


I know with Bosch.... we use six wires.
Two for activation.
Two for power.
Two are for the sounder base.
 
  #3  
Old 02-17-17, 09:32 PM
kcxj's Avatar
Member
Join Date: Sep 2006
Location: Kansas City, MO
Posts: 928
Likes: 0
Received 0 Likes on 0 Posts
You can do this with the System Sensor RRS-MOD and System Sensor 2WTA-B detectors. You will need to get approval from the local AHJ, though.

http://library.ademconet.com/MWT/fs2/4/6036.pdf
 
  #4  
Old 02-18-17, 07:55 AM
T
Member
Thread Starter
Join Date: Mar 2010
Location: usa
Posts: 610
Likes: 0
Received 0 Likes on 0 Posts
Thanks for the information.
 
 