Carrier gas furnace problem

My furnace kicks on, sometimes it will fire and occasionally it won't. It just runs (inducer), without lighting. I run the self-test feature and all 4 stages (inducer, igniter, hi-speed fan, and low-speed fan)work correctly. Any advice on what to check next?
 
  #2  
Old 02-10-16, 08:41 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
What is the model number?
 
  #3  
Old 02-10-16, 12:00 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
The inducer motor running means that the thermostat is calling for heat.

The next step in the ignition sequence is for the pressure switch to close when the inducer motor comes up to speed, which in turn turns on the hot surface ignitor.

So the probability is that the pressure switch isn't closing --- you need to check and verify that.

If it's not closing, it's VERY unlikely that the pressure switch is the problem. The pressure switch is just revealing a defect in the furnace combustion and venting system.

Check to be sure that the pressure switch tubing has no holes or cracks. Use a paper clip or small drill bit to clean out the fitting the pressure switch tubing connects to on the inducer motor housing, which can get plugged with rust or crud. Be SURE you get all the way through the fitting into the inducer motor housing!
 
  #4  
Old 02-10-16, 05:44 PM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Series 100