Testing a thermocouple


  #1  
Old 07-10-16, 09:21 AM
Geochurchi's Avatar
Member
Thread Starter
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Testing a thermocouple

Hi, what is the procedure for testing a thermocouple,I assume if I remove the cap tube from the valve I will loose the pilot.
 
  #2  
Old 07-10-16, 09:44 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Pilot on = good thermocouple.

Disconnecting the thermocouple in a working application and having the pilot light go out is one way to confirm it's good. It will take approx 60-150 seconds for the valve to snap shut.

To check with a meter you need to use the lowest DC volts scale. The thermocouple tip needs to be kept in a flame. You measure from the center button to the metal tubing. You need to measure 20 millivolts minimum.
 
  #3  
Old 07-11-16, 10:10 AM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,277
Upvotes: 0
Received 3 Upvotes on 3 Posts
In the absence of a test adapter replacing the thermocouple is probably your best course. Taking what has been described is termed an OPEN read. This can be very misleading. Your meter may show a read of say 20 millivolts. However when a CLOSED read is taken it may show as low as zero. Also without performing a closed read there is no way to obtain a DROPOUT read, meaning a check of the gas valve power unit (magnet).
 
  #4  
Old 07-12-16, 03:20 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,604
Received 28 Upvotes on 27 Posts
Does the pilot stay on? If so, the thermocouple is good - if not, replace it. Replacements are cheap and easy to install. I've never heard of performing routine testing.
 
  #5  
Old 07-13-16, 09:40 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,277
Upvotes: 0
Received 3 Upvotes on 3 Posts
You've never heard of routine testing puzzles me.
 
 