I have a Carrier Weathermaker 9200 Gas Furnace Model # 58MXA060-12112. Unit has a LH33ZS004 HSI. Unit will not fire-up on its own. Furnace fires -up and runs fine if I ignite the gas myself. As a result I have narrowed it down to the Ignitor (I think). What I am not sure of is whether it is the Ignitor, the Ignitor Relay or something else.
My first question is what is the proper way to interpret the ohm reading I get when I test the ignitor? I have read that if it is not working the ohm reading would be 0 ( no conductivity)or if the reading is not between 30-60 it is non functioning, as well as other parameters. I removed the HSI and it test's at 78.3 ohms at room temp.
My second question is how do I test that the HSI Relay is working properly and getting power to the Ignitor.
 
Sponsored Links
  #2  
Old 10-09-16, 11:02 AM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,138
Received 2 Votes on 2 Posts
HSI can fail open (infinite or very high ohms) or shorted (near zero ohms).

Measure the AC voltage across the HSI terminals (with the HSI disconnected) when it is supposed to be on. You should measure line voltage (120 volts). If you do, then the igniter is likely bad. If you don't, then problem is elsewhere upstream.
 
  #3  
Old 10-09-16, 11:07 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,742
Received 1,187 Votes on 1,098 Posts
Measure the AC voltage across the HSI terminals (with the HSI disconnected) when it is supposed to be on.
If you find voltage...... plug HSI in and check again.

A problem relay can show voltage with the HSI disconnected but not connected.
 
  #4  
Old 10-09-16, 05:06 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,499
Received 0 Votes on 0 Posts
<< I removed the HSI and it test's at 78.3 ohms at room temp. >>


THE HSI sounds like it's good.

You also need to check for 120 VAC being applied to the HSI ----if the circuit board isn't turning on the voltage, the HSI wont heat up to light the gas.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: