I have a weather king furnace and it has no lights working on mother board the furnace wont come on, the power lost the nuetral and the furnace and microwave stoped working i had the electric fixed and have power to the furnace
#2
Welcome to the forums.
I moved you to your own thread. My answer to you is the same as the other guys. You need a test meter to check for 24VAC between the R and C terminals on the control board.
This first step determines if the board is getting low voltage operating power.
Remember... when the blower door is open... there will be no power to the furnace.
It is also possible that there is a blown fuse on your control board.
You can post the model number for the board.
I moved you to your own thread. My answer to you is the same as the other guys. You need a test meter to check for 24VAC between the R and C terminals on the control board.
This first step determines if the board is getting low voltage operating power.
Remember... when the blower door is open... there will be no power to the furnace.
It is also possible that there is a blown fuse on your control board.
You can post the model number for the board.
#3
Personally, I'd check for 120 VAC from the hot wire to the neutral wire at the shutoff switch at the furnace.
If that's OK, I'd check for 24 VAC between the R and C terminal at the furnace.
If that's OK, I'd check for 24 VAC between the R and C terminal at the furnace.