American Standard Furnace 6 red flashes Code


  #1  
Old 10-18-17, 07:43 AM
M
Member
Thread Starter
Join Date: Oct 2017
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
American Standard Furnace 6 red flashes Code

I burnt out the ignitor and just replaced it. After turning the furnace on, the inducer motor kicked in but then shut off and the vent motor kicked in blowing cold air only. The ignitor won't glow. The furnace indicator LED shows 6 flashes.

Any help on troubleshooting this issue is much appreciated. Thanks.
 
  #2  
Old 10-18-17, 10:59 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Look for the codes on the inside of the door on the blower section. Lets us know what code 6 is.
 
  #3  
Old 10-18-17, 11:19 AM
M
Member
Thread Starter
Join Date: Oct 2017
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
It says 6-Flashes-115 VAC Reversed Polarity or Bad Grounding. Thanks.
 
  #4  
Old 10-18-17, 01:08 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Most likely a bad control board. What's the model number of the furnace?
 

Last edited by skaggsje; 10-18-17 at 01:10 PM. Reason: Added
  #5  
Old 10-18-17, 01:30 PM
M
Member
Thread Starter
Join Date: Oct 2017
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
I believe CNT05165 is the control board number. A little more detail, so I was cleaning the flame rod and readjusting the ignitor. I put the ignitor back on but did not line it up correctly so heat was produced and the ignitor shattered. It's now replaced, but now I have this 6 red flashes code. I wonder if the blown out ignitor did some electrical damage to the system or board.
 
  #6  
Old 10-18-17, 04:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
so heat was produced and the ignitor shattered.
Is that because the igniter touched ground ?
If yes..... more than likely the control board is damaged.
You could look at the back of it and probably see a burned spot.

Name:  as6.JPG
Views: 4981
Size:  17.4 KB
 

Last edited by PJmax; 10-18-17 at 05:16 PM.
  #7  
Old 10-20-17, 08:18 AM
M
Member
Thread Starter
Join Date: Oct 2017
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
So i replaced the circuit board and furnace is working. Lesson leant, make sure when you replace your ignitor do not let it contact anything otherwise it will burn your circuit board. Thanks for the help everyone.
 
 