Gas Furnace Start issues

Model: Ruud UGDG-10EBRJR
Thermostat: Honeywell RTH3100C

I am having issues with my furnace starting.

Sequence as follows:
-Blower fan starts
-Vent fan starts (runs for about 30 seconds)
-Element begins to glow(about 20 seconds)
-Solenoid for gas clicks, and almost immediately the element disengages and nothing ignites.

Cycle continues and will enter into lockout, then attempt to start again. When I "reset" the system ( by leaving the panel off and the switch open for about 5 minutes), the burners will ignite and stay lit. However, when it reaches the set temperature and turns off, it will not re-ignite to reheat.

In addition, the AC was running simultaneously, but I disconnected the relay for the condenser to alleviate that problem. It is temporary until I can get this all sorted out.
 
  #2  
Old 10-31-17, 10:23 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,471
Received 87 Upvotes on 80 Posts
https://customer.honeywell.com/resou.../69-2340ES.pdf

That is a heat pump thermostat. It will run the AC with a heating demand. You need a different thermostat.

It also sounds like you need a new furnace control board.
 
  #3  
Old 10-31-17, 10:54 AM
D
Member
Thread Starter
Join Date: Oct 2017
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will replace the thermostat for the right one.
 
 