Gas Furnace Start issues
Old 10-31-17, 10:04 AM
D
Model: Ruud UGDG-10EBRJR
Thermostat: Honeywell RTH3100C
I am having issues with my furnace starting.
Sequence as follows:
-Blower fan starts
-Vent fan starts (runs for about 30 seconds)
-Element begins to glow(about 20 seconds)
-Solenoid for gas clicks, and almost immediately the element disengages and nothing ignites.
Cycle continues and will enter into lockout, then attempt to start again. When I "reset" the system ( by leaving the panel off and the switch open for about 5 minutes), the burners will ignite and stay lit. However, when it reaches the set temperature and turns off, it will not re-ignite to reheat.
In addition, the AC was running simultaneously, but I disconnected the relay for the condenser to alleviate that problem. It is temporary until I can get this all sorted out.
Old 10-31-17, 10:23 AM
Houston204's Avatar
Received 95 Upvotes on 88 Posts
https://customer.honeywell.com/resou.../69-2340ES.pdf
That is a heat pump thermostat. It will run the AC with a heating demand. You need a different thermostat.
It also sounds like you need a new furnace control board.
Old 10-31-17, 10:54 AM
D
I will replace the thermostat for the right one.