Gas Boiler & Gas Hot Water Heater Carbon Monoxide Levels
#1
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Gas Boiler & Gas Hot Water Heater Carbon Monoxide Levels
Hi all.
I just got a used Bacharach Combustion Analyser but also have a Testo 320.
I was doing some Flue gas testing and the Testo was at 1PPM maybe go to 2 PPM. The Bacharach went to 90+PPM on the boiler and 75+ on the hot water heater.
Both the Testo and Bacharach have new O2 sensors.
Also, the draft is -.04 to -.06 so I know I'm good there. The heat exchangers are very clean. I had cleaned out the boiler and burners, which were clean to begin with I pulled the hot water heater burner, and vacuumed. Looked very clean also.
No vent obstructions. So, I'm wondering if the Bacharach CO sensor is hosed.
Any suggestions?