Carrier furnace won't heat, code 33


  #1  
Old 04-10-18, 05:13 PM
T
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Carrier furnace won't heat, code 33

Looking for any troubleshooting thoughts regarding my Carrier 58MCA060 furnace.

Symptoms:
  • The status light blinks 3 short, 3 long, which I understand is code 33 (limit switch). I pushed on the flame rollout switch without any effect. Ordered a new switch, just in case.
  • Filter was about 1 month old, so it was dirty but not so bad that it should have been restricting airflow.
  • The thermostat screen is blank, even though the wires are showing voltage with a multimeter. Tried replacing the thermostat, no improvement.
  • The blower for the house air is working, so there is power to the furnace, but the blower to circulate the burner air doesn't turn.
  • No indication that the burners are even trying to turn on.
  • Checked the condensation trap for a clog, flushed it out to be safe.
  • 3 amp fuse looks good, replaced it anyways to be safe.

Next step is probably going to be a call to a professional. Any thoughts on other things to check would be greatly appreciated.
 
  #2  
Old 04-10-18, 05:27 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,765
Received 4,119 Upvotes on 3,699 Posts
Welcome to the forums.

The burner will not fire with a code present.
Did you check for 24vac from R to C ?
If you don't have 24vac there.... the flame rollout sensor is tripped or the limit switch has not reset. You are interested in the limit circuit that connects pin 1 to pin 7.

Download this so you have it.... manuals online F9F9a827d0f-517a-40fd.pdf

Name:  53mca.JPG
Views: 3473
Size:  37.9 KB
 

Last edited by PJmax; 04-10-18 at 05:56 PM.
  #3  
Old 04-11-18, 03:58 PM
T
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
It ended up being the original cheap thermostat that went bad. The newer thermostat required a C wire, which was terminated on the thermostat side but I didn't notice it was not terminated at the furnace until I was investigating the circuit.

Thanks for the feedback!
 
  #4  
Old 04-11-18, 05:49 PM
R
Member
Join Date: Oct 2016
Posts: 2,183
Received 199 Upvotes on 181 Posts
So what caused the limit switch fault?
 
  #5  
Old 04-12-18, 02:21 AM
T
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
No idea. The rollout switch was not popped out, but maybe it had also gone bad? It's possible that both the switch and thermostat needed replacing, although the chances of 2 pieces of hardware failing at the same time is pretty slim.
 
 