Ice built up, furnace locked out


  #1  
Old 01-22-19, 04:32 AM
X
Member
Thread Starter
Join Date: Mar 2009
Location: Albany, NY
Posts: 212
Received 0 Upvotes on 0 Posts
Ice built up, furnace locked out

I had this concern for a while, but since it never caused a problem I left it alone:

Ice builds up at furnace exhaust

That is until yesterday, on the worst possible day! Install is 9 years old at this point and I don't expect the original installer to take care of it. I don't want to mess around with the roof, so if I was to make it right myself, would it be easier just to vent it to the side, at least the exhaust pipe?
 
  #2  
Old 01-22-19, 05:37 AM
X
Member
Thread Starter
Join Date: Mar 2009
Location: Albany, NY
Posts: 212
Received 0 Upvotes on 0 Posts
Well, the installer said they will look at it, and also agreed that there shouldn't be two 90 degree elbows. Exhaust should be straight and not shooting into the cap.
 
  #3  
Old 02-07-19, 04:21 PM
X
Member
Thread Starter
Join Date: Mar 2009
Location: Albany, NY
Posts: 212
Received 0 Upvotes on 0 Posts
I got it "fixed" for free, but it sticks out as a sore thumb by more than a foot. Could I cut it off past the cap?

 
  #4  
Old 02-07-19, 08:29 PM
R
Member
Join Date: Oct 2016
Posts: 2,183
Received 199 Upvotes on 181 Posts
Is the exhaust still shooting up into the cap?
 
  #5  
Old 02-07-19, 08:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
You can paint but I wouldn't recommend cutting it. The two lines need to be that far apart.
 
  #6  
Old 02-07-19, 09:19 PM
X
Member
Thread Starter
Join Date: Mar 2009
Location: Albany, NY
Posts: 212
Received 0 Upvotes on 0 Posts
It's shooting on the side as seen on the picture. The intake is pointing the other way.
 
  #7  
Old 02-08-19, 10:15 PM
M
Member
Join Date: Feb 2019
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
All I can tell this is very ugly installation.... check the manufacturer manual for the equipment n call back your installer and teach him to read the manuals prior to attempt any installation.
 
  #8  
Old 02-08-19, 10:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
The problem is there are two PVC lines...... fresh air in and exhaust inside the chimney.
The furnace requires minimum spacing between the two.
 
  #9  
Old 02-09-19, 04:19 AM
X
Member
Thread Starter
Join Date: Mar 2009
Location: Albany, NY
Posts: 212
Received 0 Upvotes on 0 Posts
I think I'll just remove this completely and take the exhaust to the side of the house.
 
 