Furnace problem


  #1  
Old 02-17-19, 11:11 AM
S
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Furnace problem

When I set the thermostat to call for heat, the inducer motor will start, the spark igniter would continually spark and there would be a pilot flame however, the valve would not open and the burners will not light. So I tried replacing the flame sensor about a month ago, and it was fine for about a month. But then now the same thing is happening. Is this because of a problem in a control module?
 
  #2  
Old 02-17-19, 11:33 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Welcome to the forums,

You posted in the workshop heater area. Is this your home furnace ?
A make and model of your unit would be very helpful.

With an intermittent spark ignition system..... the pilot must be lit and be a good sized flame for the furnace to open the main gas valve.
 
  #3  
Old 02-17-19, 08:16 PM
S
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you, the model number is FBF050B12A3
The control panel model that I am using is an S8600M made by honeywell
 
  #4  
Old 02-17-19, 10:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
That's an ICP furnace.
The S8600M is the intermittent ignition module

The original S8600M didn't have a separate flame sensor. It had an igniter/sensor rod. More than likely...... your problem is going to be with a dirty igniter/pilot assembly. It needs to be taken out and cleaned. The pilot orifice also needs to be cleaned.

ICP furnace
 
 