Gas furnace won't start
Greetings. We have a Sears furnace manufactured by Inter-City Products - photos attached.
Although 25 years old, much of the furnace has been recently upgraded - like within the past 5 or so years - new main blower, new heat exchanger, new 1F80-261 thermostat/control etc. Also new AC two years ago.
Anyway I tried starting it up for the fall, I can hear it click but the gas and blowers don't click on.
I went through the instructions on the inside panel, cut the electricity then turned off the gas valve shown in the photo - waited 5 minutes then turned it on, restored electricity and tried again to start. Still hear clicking in a relay - but no start up.
Any ideas? I was wondering if the blower in the pic is dead? Or maybe the semiconductor on that blower?
Any advice appreciated.
Although 25 years old, much of the furnace has been recently upgraded - like within the past 5 or so years - new main blower, new heat exchanger, new 1F80-261 thermostat/control etc. Also new AC two years ago.
Anyway I tried starting it up for the fall, I can hear it click but the gas and blowers don't click on.
I went through the instructions on the inside panel, cut the electricity then turned off the gas valve shown in the photo - waited 5 minutes then turned it on, restored electricity and tried again to start. Still hear clicking in a relay - but no start up.
Any ideas? I was wondering if the blower in the pic is dead? Or maybe the semiconductor on that blower?
Any advice appreciated.
Last edited by PJmax; 10-08-19 at 10:02 AM. Reason: resized pictures
#2
Welcome to the forums.
They replaced a heat exchanger on a 20+ year old furnace ??
The large item in your pictures is the gas valve.
The draft inducer blower looks to be in the bottom of the last picture.
You have an intermittent pilot ignition...... is it the spark type ?
There are two safety switches on the front of the furnace. One is directly behind the gas valve. It's connected with two red wires. The other one is in the heat exchanger area. If either of these two are open.... the draft inducer won't start and you'll not get ignition. You'll need to check these switches with a voltmeter if the furnace is on or an ohmmeter if the power is turned off.
The link below is part one of your manual. At the bottom of the page is a link for part two.
Part one - Service manual (pdf)
They replaced a heat exchanger on a 20+ year old furnace ??
The large item in your pictures is the gas valve.
The draft inducer blower looks to be in the bottom of the last picture.
You have an intermittent pilot ignition...... is it the spark type ?
There are two safety switches on the front of the furnace. One is directly behind the gas valve. It's connected with two red wires. The other one is in the heat exchanger area. If either of these two are open.... the draft inducer won't start and you'll not get ignition. You'll need to check these switches with a voltmeter if the furnace is on or an ohmmeter if the power is turned off.
The link below is part one of your manual. At the bottom of the page is a link for part two.
Part one - Service manual (pdf)
#4
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
...When I put my hand on the back side of that gas valve block - the block where the light blue colored on-off dial is located for the gas shown in the first pic (I assume that is what you refer to as the gas valve), I can't feel any switch...
Do I need to remove that other panel behind the gas valve to access the heat exchanger switch?
I think it might be a spark type - there is no pilot light to light.
Do I need to remove that other panel behind the gas valve to access the heat exchanger switch?
I think it might be a spark type - there is no pilot light to light.
#5
When the furnace lit previously..... did you hear a sparking sound at the start ?
Look at the two valve pictures. The two red wires that look like they're coming out of the bottom of the valve are connected to the limit. Follow them.
In the third picture.... I'm pretty sure the four wires on the right are the limit wires. There are the two red's that go to the limit under the gas valve and the two blues go to the other limit.
The limit switch on the red wires will probably be like the one in the link below.
The other limits won't have the red reset button.
Nordyne limit - rollout
Look at the two valve pictures. The two red wires that look like they're coming out of the bottom of the valve are connected to the limit. Follow them.
In the third picture.... I'm pretty sure the four wires on the right are the limit wires. There are the two red's that go to the limit under the gas valve and the two blues go to the other limit.
The limit switch on the red wires will probably be like the one in the link below.
The other limits won't have the red reset button.
Nordyne limit - rollout
#6
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If by switch you mean the rectangular black block shown above the gas valve block - the black box with the two red wires attached, I did put an ohm meter across the two contacts and the switch seems to be closed - when the power to furnace is off...I got a low ohm reading..
Last edited by PJmax; 10-08-19 at 12:25 PM. Reason: reoriented/resized picture - added labeling
#9
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I followed the two red wires you mentioned - the wires that look like they are coming out of the gas valve but are actually coming out of the second component mounted to that plate. The first pic in this post shows them...one of the wires goes to the semiconductor shown in the second pic - that component is mounted to the blower. The second wire shown in the first pic in this post goes up to that rectangular block with the two red wires going into it.
These two pics should have also been rotated 90 degrees clockwise sorry.
These two pics should have also been rotated 90 degrees clockwise sorry.
Last edited by tetra; 10-08-19 at 12:33 PM. Reason: resized/labeled pics
#10
Check the two switches for continuity. They should be shorted.
There's the spark ignition module.
There's the spark ignition module.
#11
with the inducer not coming on, you should see if power is being applied to it and then check the control circuit upstream if it isn't getting power.
Can you post a clear pick of the schematic. usually on the blower access panel.
Can you post a clear pick of the schematic. usually on the blower access panel.
#13
That diagram is slightly different then the service manual.
The limits were moved to a different parts of the circuit.
The limits were moved to a different parts of the circuit.
#16
I was using a different diagram. Same model number but a lower revision. The limit switches are moved to a different circuit and don't stop the inducer from starting.
The next logical step is to check for 120vAC on the white and black draft inducer motor wires during a call for heat.
The next logical step is to check for 120vAC on the white and black draft inducer motor wires during a call for heat.
#17
I was using a different diagram. Same model number but a lower revision. The limit switches are moved to a different circuit and don't stop the inducer from starting.
I can't see how the limits stop the unit from firing. With system relay low voltage side closed and pressure switch closed, there's a direct circuit to the module.
edit: nevermind, they cut power to the thermostat.
Last edited by user 10; 10-08-19 at 01:43 PM.
#19
yes.
you need to turn on the heat and see if that motor is getting power with a meter.
you can also feel the motor and see if it's warm after a minute or so.
the brown wires lead to a capacitor. A bad cap can cause the motor to not start - if the motor is getting power, getting warm and not turning over it's worth trying a new capacitor before changing the entire assembly.
you need to turn on the heat and see if that motor is getting power with a meter.
you can also feel the motor and see if it's warm after a minute or so.
the brown wires lead to a capacitor. A bad cap can cause the motor to not start - if the motor is getting power, getting warm and not turning over it's worth trying a new capacitor before changing the entire assembly.
#21
Can we assume that you have the blower door on or the switch held in and heard the relay close when the heat was called for ?
This is a basic circuit. There is a system relay that closes when the thermostat calls for heat. The blower black wire goes to terminal 3. Terminal 5 should be live 120v at all times. The white wire goes directly to neutral splice.
Check from 3 and check from 5 to white wire when relay is closed. If ok on 5 and not on 3.... the relay is bad or it's not closed. There would be 24vAC on terminals 7 and 8 if the stat was calling for heat.
This is a basic circuit. There is a system relay that closes when the thermostat calls for heat. The blower black wire goes to terminal 3. Terminal 5 should be live 120v at all times. The white wire goes directly to neutral splice.
Check from 3 and check from 5 to white wire when relay is closed. If ok on 5 and not on 3.... the relay is bad or it's not closed. There would be 24vAC on terminals 7 and 8 if the stat was calling for heat.
#22
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Are draft inducers for this furnace hard to find and or expensive?
I am thinking its the draft inducer because the inducer motor hums when getting power...when i toggle the thermostat on that is...
I am thinking its the draft inducer because the inducer motor hums when getting power...when i toggle the thermostat on that is...
#24
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes Pjmax I am pretty sure the relay closed when the heat was switched on - I heard a clicking. The blower door was on and I think there is a switch that closes when that lower door is on.
#25
Are draft inducers for this furnace hard to find and or expensive?
I am thinking its the draft inducer because the inducer motor hums when getting power...when i toggle the thermostat on that is...
I am thinking its the draft inducer because the inducer motor hums when getting power...when i toggle the thermostat on that is...
It may be the capacitor that's bad, follow the brown wires.
How were you checking for power?
#27
you may have had your meter set to the wrong mode or the lead didn't make proper contact.
The cap is measured in mf, not volts.
the cap should be totally discharged by the motor winding after power is removed. you discharge it as a precaution and then check the capacitance.
if your meter doesn't check capacitance, just change the capacitor first, they're cheaper than the meters that can measure mf.
The cap is measured in mf, not volts.
the cap should be totally discharged by the motor winding after power is removed. you discharge it as a precaution and then check the capacitance.
if your meter doesn't check capacitance, just change the capacitor first, they're cheaper than the meters that can measure mf.
#28
Member
Thread Starter
Join Date: Oct 2019
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
...come to think of it though, when I checked voltage across the motor - I had that lower blower door off and that safety switch was not closed so I guess it was not getting power because of that. I forgot about that LOL.
Checked it again today and I think I closed that switch and the motor was humming then.
Checked it again today and I think I closed that switch and the motor was humming then.