Cad cell


  #1  
Old 11-05-23, 02:52 PM
R
Member
Thread Starter
Join Date: Nov 2023
Posts: 2
Received 0 Upvotes on 0 Posts
Cad cell

The cad cell in my oil burner works when I shine a flashlight on it, but when I reinstall it, the furnace locks out after the 30 seconds. Do they wear down, or are they an all or nothing item? I have 2 used ones. Both give the same result. Fine with a flashlight, but relay trips when installed.
 

Last edited by Ray-Davies; 11-05-23 at 02:53 PM. Reason: Spelling
  #2  
Old 11-06-23, 02:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,963
Received 4,148 Upvotes on 3,725 Posts
Welcome to the forums.

You're going to need a meter to make tests. Nothing complicated.
You may have a burner or air mixture issue.
You need to test the cell in operation.

Required..... a meter with test clips and a clip to clip.
You can just wrap the cell wires around the test probes.
Use a piece of thin wire to jumper Fs to Fs.

Rather than type up a test... check out this video.... Testing cad cell system - video
 
Ray-Davies voted this post useful.
  #3  
Old 11-07-23, 07:34 PM
R
Member
Thread Starter
Join Date: Nov 2023
Posts: 2
Received 0 Upvotes on 0 Posts
Thanks Pete
 
 