No heat or cooling on heat pump

I have a Coleman heat pump Model SSZ140301 and furnace GMH950703BX the unit has stopped working, I was trying to trouble shoot the problem and found that the defrost board had three resisters so hot that they would burn you fingers so assuming the board was bad replace it and steal having the same problem.

When I disconnect the low side pressure switch the problem of the hot resisters goes away, with the LPS connected, when you energize the 24V transformer after a period of four or five minutes the transformer get hot, have burnt one up so far, so installed a 3A fuse in the 24V side I am assuming that there is a dead short but have been unable to find one, have disconnected wires going to heat pump and checked for shorts, have isolated thermostat completely from the system also replaced the contact switch in the heat pump, I have checked the wires on the LPS to ground. Any help would be greatly appreciated.
 
Sponsored Links
  #2  
Old 05-28-16, 10:09 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,805
Received 1,194 Votes on 1,105 Posts
Welcome to the forums.

Your equipment is Goodman.

It sounds like you have a shorted contactor coil. The link below should be the one your unit uses. There are many different replacements that will replace that one.

Contactor CONT2P025024VS Repair Clinic


In the picture below I labeled where the 24vac connects on each side of the contactor. Turn power off to the condensor. The contactor is powered from the furnace. Disconnect the two 24vac wires and see if your short is gone. You can also measure the resistance of the contactor coil.... it should be around 10-15 ohms.

Name:  gc.jpg
Views: 102
Size:  23.9 KB
 
  #3  
Old 05-31-16, 10:52 AM
D
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks for you reply. I had already replace the contact switch it was bad. Finally found the problem had a short in the thermostat wire checked it several time don't know how I missed it. Thanks again
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: