Basic wiring questions
#1
Member
Thread Starter
Join Date: Sep 2017
Location: United States
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Basic wiring questions
https://i.imgur.com/a9nfYjb.jpg
I'm putting a new furnace in and I'm at the point to wire it in. I was going to use the existing wiring which i think is 10-3. My main question is about where the neutral goes or if i need different wiring for this furnace. I dont see a neutral bar or spot to put it.I'll post a picture that shows what im working with. Let me know if you need any additional information.
thanks in advance.
I'm putting a new furnace in and I'm at the point to wire it in. I was going to use the existing wiring which i think is 10-3. My main question is about where the neutral goes or if i need different wiring for this furnace. I dont see a neutral bar or spot to put it.I'll post a picture that shows what im working with. Let me know if you need any additional information.
thanks in advance.
Last edited by PJmax; 09-26-17 at 10:07 AM. Reason: added pic from link
#2
Member
The link doesn't work. So I'll just take a guess, the furnace won't have a neutral bar ?? What's the make and model number ?
#3
Member
Thread Starter
Join Date: Sep 2017
Location: United States
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Its a goodman aruf with a 10kw heat kit. I didnt remove the old furnace so I'm not sure about the wiring. I'm thinking maybe i just need two wire instead of three. I copied the link and it worked for me.
#4
Welcome to the forums.
You are in trouble.
That new electric furnace requires at least 45A of power based on the 10kw heater. #10 is only good for 30A. There is no neutral bar or connection as that unit strictly needs 240VAC. That would be two hots and a ground.
That 10-3 is going to need to be replaced with 6-2 w/ground cable.
You are in trouble.
That new electric furnace requires at least 45A of power based on the 10kw heater. #10 is only good for 30A. There is no neutral bar or connection as that unit strictly needs 240VAC. That would be two hots and a ground.
That 10-3 is going to need to be replaced with 6-2 w/ground cable.