Replacing reversing valve solenoid


  #1  
Old 12-05-18, 10:08 AM
G
Member
Thread Starter
Join Date: Oct 2015
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Replacing reversing valve solenoid

Model CH5524VKA2
Goodman compressor
25 years old
Seems to have a problem going in or coming out of defrost mode intermittently. I shut it down at the thermostat and restart it 5 minutes later and it's ok for a week or more.I thought I'd try to replace the solenoid. Is it just a matter of disconnecting the wires, removing a nut and pulling it out?
 
  #2  
Old 12-05-18, 01:17 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,081
Received 161 Upvotes on 147 Posts
Hi, as far as I know a solenoid coil is either good or bad , there is no in between , the problem is in the circuit that controls it.
Geo
 
  #3  
Old 12-05-18, 04:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,063
Received 3,973 Upvotes on 3,566 Posts
Welcome to the forums.

Yes.... that's all there is to it but I agree with Geo..... those valves don't usually go intermittent.
I'd check the voltage to it first and make sure you aren't loosing that.
 
  #4  
Old 12-06-18, 10:02 AM
G
Member
Thread Starter
Join Date: Oct 2015
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Great, thank you both. I'll check voltages and probably try a new defrost control board.
 
 