Aprilaire 600 automatic wiring to Carrier 59TP6 furnace - Need Check


  #1  
Old 09-16-16, 08:56 PM
H
Member
Thread Starter
Join Date: Sep 2016
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Aprilaire 600 automatic wiring to Carrier 59TP6 furnace - Need Check

Hello,

I am installing an Aprilaire 600 automatic humidifier to Carrier Performance 96 furnace. Can someone please help me with the wiring or check if this is correct?

Humidistat: Furnace: Solenoid (Humidifier):

R -------------------------R
C--------------------------COM 24V------------------------S
W-------------------------W/W1
gf (not used)
G (not used)
H--------------------------HUM 24V
H------------------------------------------------------------S
ODT---outdoor sensor
ODT---outdoor sensor

Can you please check if this is correct.

Thank-you
 
  #2  
Old 09-16-16, 09:12 PM
H
Member
Thread Starter
Join Date: Sep 2016
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
or should it be like this:
Humidistat: Furnace: Solenoid:
R -------------------------R
C--------------------------COM 24V
W-------------------------W/W1
Gf (not used)
G (not used)
H--------------------------COM 24V
H------------------------------------------------------------S
ODT---outdoor sensor
ODT---outdoor sensor
HUM 24V------------------------S
 
  #3  
Old 09-16-16, 09:36 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Welcome to the forums.

This method will work.....
Humidistat: Furnace: Solenoid (Humidifier):

R -------------------------R
C--------------------------COM 24V------------------------S
W-------------------------W/W1
gf (not used)
G (not used)
H--------------------------HUM 24V
H------------------------------------------------------------S
ODT---outdoor sensor
ODT---outdoor sensor


An alternate way it can be connected if your thermostat is set up for two stage heat. ......

R -------------------------R
C--------------------------COM 24V------------------------S
W------------------------- HUM 24V
gf (not used)
G (not used)
H-------------------------- R (jump to R)
H------------------------------------------------------------S
ODT---outdoor sensor
ODT---outdoor sensor
 
  #4  
Old 09-17-16, 10:32 PM
H
Member
Thread Starter
Join Date: Sep 2016
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you so much
Is there an appreciation button?
 
  #5  
Old 09-17-16, 10:47 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Nope.... the thanks is appreciated. Good luck.
 
  #6  
Old 10-07-16, 06:55 PM
H
Member
Thread Starter
Join Date: Sep 2016
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank-you PJMax for your help.

I installed the humidifier today and everything works fine.

The first method that you mentioned was the one I used.
 
  #7  
Old 10-07-16, 07:40 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Thank you for stopping back and letting me know how it worked out.
 
 