Connect humidifier to nest 3rd Gen Thermo Stat.


  #1  
Old 04-08-18, 04:21 PM
D
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 9
Received 0 Upvotes on 0 Posts
Connect humidifier to nest 3rd Gen Thermo Stat.

Hello All,

I came across this forum after doing some google searching and it looks like PJmax is very knowledgeable and helpful on the subject of humidifiers and thought I would see about getting some help.

I have a new Nest 3rd Gen thermostat and I would like to have it control my humidifier. My current humidifier has a manual control and I believe it is a bypass system as duct work comes out of the air handler around the back and then into the humidifier which is connected to the return I believe.

I'm not sure if I just need to connect the red and white wires from the manual control to the nest or not.

Here's a few photos of how it is currently wired.

Air Handler:
Name:  0408181700_resized.jpg
Views: 417
Size:  85.8 KB

Transformer I believe ?:
Name:  0408181421a_resized.jpg
Views: 411
Size:  86.2 KB
Name:  0408181657_resized.jpg
Views: 340
Size:  89.3 KB

Wiring at the Humidifier:
Name:  0408181829_resized.jpg
Views: 451
Size:  94.6 KB


Wiring at the humidistat:
Name:  0408181704_resized.jpg
Views: 374
Size:  92.8 KB

Humidifier Model:
Name:  0408181830_resized.jpg
Views: 291
Size:  89.6 KB


Any thoughts on how to wire this to the Nest thermostat would be helpful.

Thanks.
 
  #2  
Old 04-08-18, 04:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
Welcome to the forums.

This is a basic setup. The two brown wires on the solenoid go to C on the furnace board and * on the nest. That's it. Absolutely nothing else in line.
There is no polarity as this is AC.

Name:  hn.jpg
Views: 310
Size:  42.9 KB
 
  #3  
Old 04-08-18, 05:09 PM
D
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 9
Received 0 Upvotes on 0 Posts
Thanks for the crazy fast reply. I don't have a C port on the air handler board.

Here's what I got.

On the nest, my blue wire is plugged into the C port. So Im guessing the C wire plugs into the B port on the air handler?
 
Attached Images   
  #4  
Old 04-08-18, 05:30 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
On that Trane control board..... B is the common terminal.
 
  #5  
Old 04-08-18, 05:54 PM
D
Member
Thread Starter
Join Date: Apr 2018
Location: United States
Posts: 9
Received 0 Upvotes on 0 Posts
Thank you so much for your help.

One last question I think: should this setting on the Nest be set to Hum. only or Hum. + heat to the right of Activate.

I think it should be set to Hum. + heat, but just want to make sure.

Edit: it looks like humidifier only lets me control the humidifier independently by itself. Humidifier + Heat turns it off and on only when the heater is running.
 
Attached Images  

Last edited by duke69111; 04-08-18 at 06:13 PM.
  #6  
Old 04-09-18, 02:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
I think it should be set to Hum. + heat, but just want to make sure.
That's how I set it up. I only want the humidifier to run when the heat is on.
 
 