Bathroom exhaust fan won't work.


  #1  
Old 11-05-16, 02:39 PM
C
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Bathroom exhaust fan won't work.

My bathroom exhaust fan has stopped working. It's got three switches on the wall, Vent, heat, and light. None of these functions work. Is it a bad breaker? And how do I find out with a voltage tester?
 
  #2  
Old 11-05-16, 03:06 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
I would guess a tripped breaker or a tripped GFCI receptacle.
Look for any GFCI's in the house and push test and reset.
Also reset the suspected breakers. Some breakers might appear to be fine when tripped.
 
  #3  
Old 11-05-16, 03:19 PM
C
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have done that, but still not working. Is it a possible bad breaker?
 
  #4  
Old 11-05-16, 03:37 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's possible. Voltage testers are not recommended. Use a meter, analog preferred.

The breaker's hot terminal should read ~120V to both neutral and ground.
 
 