Leaking cast iron to PVC boot


  #1  
Old 01-07-18, 05:42 PM
A
Member
Thread Starter
Join Date: May 2017
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Leaking cast iron to PVC boot

One of the 2 stacks in my house has started leaking, and was discovered during a recent extreme cold spell (regularly -0 F) in Indiana. (short version of house: 1920 built house. countless remodels to subdivide... current one to restore to a single family home in progress by me).

I'm not sure when the leak started, but it was discovered when the paint started bubbling on the wall in the 1st floor bathroom. Above the 1st floor bathroom is the 2nd floor bathroom. I opened up the ceiling access panel between the 1st and 2nd floor, and saw the rubber joint between the cast iron and PVC has started leaking.
Name:  LeakingJoint.jpg
Views: 1886
Size:  11.9 KB
Closeup:
Name:  LeakingJointCloseup.jpg
Views: 1454
Size:  10.6 KB

Going to the basement, I discovered this:
Name:  FrozenStackBasement.jpg
Views: 1378
Size:  13.9 KB

The leak had flowed down the wall, froze as it went, and then accumulated frozen at the base of the stack. The stack runs along an uninsulated exterior wall. I chipped away and and put a space heater in to ensure the base-stack wouldn't freeze.

As things thaw out (as they are doing now) I'll have a water logged drywall and insulation to tear out and replace, as well as the stack to repair. See main floor bathroom pic:
Name:  bathroomWall.jpg
Views: 794
Size:  7.9 KB

2 questions:

1. Is having a drain stack on an uninsulated exterior wall ever ok, or should I move it? I could re-route to another drain stack that goes to another bathroom on the 2nd floor (that's on an interior wall).

2. If I keep the drain stack, what's the recommendation to repair the joint? Replace the cast iron T with a PVC one, like this? I'm not sure the cast iron T is advisable to keep using as there's evidence of past leaks...
 
  #2  
Old 01-07-18, 06:32 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
One problem is the flexible coupling used. You need a jacketed no-hub coupling.
Assuming the pipe is 3", something like this:
https://www.homedepot.com/p/3-in-EPD...0-33/100372287

Fernco identifies cast iron as 'cast iron' or 'extra heavy cast iron'. If the P3000-33 doesn't fit snug, a P3005-33 might.
 
 