gas line pressure test


  #1  
Old 11-15-18, 08:31 AM
A
Member
Thread Starter
Join Date: Oct 2016
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
gas line pressure test

I am finishing my basement and installing 3 new gas lines for range, gas fireplace and outdoor grill. I have all the lines run, but have not yet connected into the existing service at the house. I am pressure testing all the new work first and it does hold 15 psi for 15 minutes. It will even hold 15 psi for 3 hours, but when I check it the next day, the pressure is down to almost 0. To me, I would assume it would hold the pressure indefinitely. When I bubble test, I can't find anything.

Is this expected behavior, and thats why the inspectors will only look at the 15 minute test?
 
  #2  
Old 11-15-18, 04:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,877
Received 3,749 Upvotes on 3,362 Posts
The pressure will vary greatly based on the temperature.
 
  #3  
Old 11-17-18, 11:10 AM
steve_gro's Avatar
Member
Join Date: Jan 2004
Location: San Francisco
Posts: 967
Upvotes: 0
Received 1 Upvote on 1 Post
Is it steel pipe or csst? If it's steel (and not connected to anything) pump it up to 100 psi (or whatever you can manage) then spray. I don't know what the max would be for csst. Note that a plumbing supplier will carry bubble stuff that lasts longer than dish soap (doesn't evaporate as quickly).
 
 