Thermostat C wire to RobertShaw 780-715 ICU
Received 0 Votes
I have a gas furnace (no A/C) with a RobertShaw 780-715 U Ignition Control Unit. I have a 4-wire bundle coming into the furnace from the wall thermostat. Only 2 wires are being used (red and white). I'd like to use one of the extra wires in the bundle to use as a common wire (c-wire) in order to power one of those new thermostats (Echo, Nest, etc). Below is my crude drawing. Where do I connect the third wire to create a C-wire?
PJ is showing the safest way to do it.
It appears that the ground is connected internally to the TR and MV/PV terminals on the unit. I can't verify it but if so you are correct that you could connect C to the TR terminal. Is there a wiring diagram for the furnace? I would expect it to show that the transformer be attached to TR with the gas valve connected to MV/PV. And a wire from the ground terminal to the furnace chassis.
Astuff is correct. All three terminals are connected together inside the module.
We "could" use that connection or you could even connect your C wire to chassis.
I like connecting C right at the source for the thermostat.
Received 0 Votes
Thank you again.
I finally did the wiring adjustment to create a "C" wire, as recommended in PJ's mark'ed up diagram. I then hooked up a cool , Echo Bee smart thermostat. Works great! Just wanted to thank you again. No way I could have figured this out on my own even with the wiring diagram in the furnace.
-James
-James