Nest 3rd Gen Cooling Stage 2 not working but Heat pump cooling is working

I spent more than an hour with Nest tech support but they were not able to fix this issue. They are sending me a new base, but I don't think that will resolve the problem. I have a Goodman heat pump and a Nest 3rd Gen tstat. The Cooling Stage 2 does not provide cold air, but when I run a test, the Heat Pump Cooling works fine. The compressor and fan are both running for Cooling Stage 2 but the air is not cold. I suspect that the reversing valve is not opening. Any thoughts on programing changes that will get the system working. As mentioned above, the Heat Pump Cooling works perfect.

Thanks, Will
 
Sponsored Links
  #2  
Old 05-05-18, 01:02 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Votes on 0 Posts
Are you sure you have a 2 stage compressor? What is the model # on the outside unit?
 
  #3  
Old 05-05-18, 01:09 PM
W
Member
Thread Starter
Join Date: May 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Unfortunately, I can't read the Model number. It's worn off. However, I have two yellow wires to the tstat
 
  #4  
Old 05-05-18, 01:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,719
Received 1,184 Votes on 1,096 Posts
Welcome to the forums.

You're saying it cools fine in stage 1 but not stage 2 ??
That wouldn't be a reversing valve issue. Same valve operates in both stages.
 
  #5  
Old 05-05-18, 01:14 PM
W
Member
Thread Starter
Join Date: May 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Yes, G, Y1 works well, but G Y1, Y2 does not work. The compressor and fan are running with G, Y1, Y2 but the air is not cold. I suspect the reversing valve is not opening.
 
  #6  
Old 05-05-18, 01:29 PM
W
Member
Thread Starter
Join Date: May 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Thanks for the feedback. I just unplugged the Y2 wire and it seems to be working well. Not sure why that wire is needed.
 
  #7  
Old 05-05-18, 01:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,719
Received 1,184 Votes on 1,096 Posts
We'd need further info on the condenser to comment further.
You can look down inside from the top and see if there are two compressors.
You can let us know what low voltage wiring is connected outside.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: