Abs or pvc schedule 40 water heater down pipe

On an electric water heater can I use pvc as the downpipe to the pan?
The heater cobra with a plastic horizontal pipe that I'm supposed to connect to with a threaded connector and then glue the pipe but I've seen some posts saying it's not rated for the heat at 140F
 
  #2  
Old 12-25-17, 06:48 AM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 9,745
Received 1,210 Upvotes on 1,098 Posts
PVC is not rated for hot water use but this application is different.

Every unit that I have seen uses copper. CPVC is good for hot water.

There is probably a code the guys will comment on!
 
  #3  
Old 12-25-17, 08:13 AM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
They're all electric here so maybe not as hot? None of them in Canada have copper. Probably cpvc
 
  #4  
Old 12-25-17, 10:17 AM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
I find it odd that pvc is used in all waste outlets and you can run hot water from the faucet directly into them and pour cooking water in them but it's not rated for hot water. Presumably it's the continuous contact? A pressure relief valve is unlikely to open continuously is it?
 
  #5  
Old 12-25-17, 10:48 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
I don't know anything about codes in Canada but in the US the discharge piping from the T&P (safety) valve must be able to withstand the temperature of the water. That means either metal or CPVC. No ABS or PVC.
 
  #6  
Old 12-25-17, 01:01 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
To play it safe I would run 3/4" copper or CPVC. The drain line must be gravity fed (to the outside in California).
The PRV valve may never release but when it does you want the very hot water to exit as fast and easy as possible with no back pressure.
 
 