Vacuum Breaker


  #1  
Old 11-17-19, 07:51 PM
T
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 708
Received 69 Upvotes on 64 Posts
Vacuum Breaker

Does a vacuum breaker on a water heater have to be vertically above the inlet of a top feed water heater or can it be inline on the supply line. Most pic I've seen have the supply line go into a T with the vacuum breaker coming in from the top, and the H20 heater connection connecting from the bottom. I'd prefer to put it inline so I can use a flex copper line to make the connection to the tank as I won't have the exact location of the new H20 heater inlet.
 
  #2  
Old 11-19-19, 05:30 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
I have never heard of a vacuum breaker on a water heater installation before. Got any pictures?
 
  #3  
Old 11-19-19, 09:26 PM
T
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 708
Received 69 Upvotes on 64 Posts
Just quick google examples....there out there, but I've never seen one either. My niece in San Antonio said her plumber said they are code.

IAPMO

https://aws1.discourse-cdn.com/inter...ffc4aa70d.jpeg

https://www.aliexpress.com/item/32297423680.html
 
  #4  
Old 11-19-19, 11:49 PM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 9,747
Received 1,209 Upvotes on 1,098 Posts
ZA-15 Vacuum Relief Valve should be installed at the highest point of the cold water inlet
I have one on my chlorine storage tank, as long as it's above the tank, in theory it would open in the event that the water drained away before the level dropped into the tank and collapsed it!
 
  #5  
Old 11-20-19, 08:11 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
Just quick google examples....there out there, but I've never seen one either. My niece in San Antonio said her plumber said they are code.

Ok, I've now heard of it, but still have never seen one.

If the water heater is installed above fixtures, there is a possibility of siphonage from the water heater. If the water supply is turned off or pressure drops as fixtures are being used, there is a possibility of a siphon being created because of the fixture water supply opening being lower than the tank. This could result in the tank emptying and possible steam being created in the tank. There have been instances where this siphonic action has been so powerful as to collapse the tank. For these reasons, a vacuum relief valve must be installed
I suppose if a water heater was installed in an attic one would be required.
 
  #6  
Old 11-20-19, 08:29 AM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 9,747
Received 1,209 Upvotes on 1,098 Posts
I suppose if a water heater was installed in an attic one would be required.
Remember, you have a fixture at the bottom of the tank (the drain)!
 
 