Septic tank leach field for RV use

Reply

  #1  
Old 10-27-16, 10:01 AM
S
Member
Thread Starter
Join Date: Oct 2016
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
Septic tank leach field for RV use

I have a septic tank that will be used exclusively to dump RV grey and black water. The tank was already in place when we bought the property. It had never been used as the former owner was preparing to hook it up to a mobile home but that never occurred.

The problem is that the outlet pipe was improperly installed and there was no leach field installed. It was simply a single perforated pipe placed in the ground. It appears it was even placed at an angle so if anything is put into the septic tank the water pretty much just drains at the outlet of the tank.

There are no zoning laws or inspections in this area so that is how they got away with doing it this way. We intend to dig out the area and put in a small leach field but are somewhat uncertain as to what to do.

The RV tanks will be dumped into the tank 4-6 times per year. The soil is quite sandy. I only have a roughly 4' - 5' wide area I can use for the leach field at least for some distance.

Any suggestions/recommendations are welcome.
 
Sponsored Links
  #2  
Old 10-27-16, 11:10 AM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,575
Received 94 Votes on 83 Posts
Welcome to the forums.

Just about nothing is regulated more tightly than a septic system. I would start with the local AHJ.
 
  #3  
Old 10-27-16, 11:29 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 23,740
Received 630 Votes on 582 Posts
Contact your counties Health or Environmental Services Dept. They should have a record of what was installed and what it is approved for.
 
  #4  
Old 10-27-16, 12:39 PM
S
Member
Thread Starter
Join Date: Oct 2016
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
Unfortunately there is no such organization in the county we are located in.

We are thinking we should dig out the area, lay down a level base of gravel, place 2 or 3 perforated pipes, cover with more gravel and a layer of professional grade weed blocker and cover with dirt.

Does this seem reasonable?
 
  #5  
Old 10-27-16, 01:12 PM
M
Forum Topic Moderator
Join Date: Mar 2005
Location: USA - N.E.Tn
Posts: 47,654
Received 321 Votes on 285 Posts
How big is the RV tank? The drain field doesn't see any effluent until the tank fills, once the tank fills any thing that goes in causes the water in the tank [drawn up from the bottom half] to enter the drain lines. You'd need enough drain line to disperse the amount of additional liquid being dumped into the tank.
 
  #6  
Old 10-27-16, 01:50 PM
V
Member
Join Date: Jan 2010
Location: North East Kingdom of Vermont
Posts: 2,533
Received 1 Vote on 1 Post
Originally Posted by SunnyCamp
". . . I only have a roughly 4' - 5' wide area I can use for the leach field . . ."
Is that right along the Property Line ?

How large is the entire Parcel that's involved ?

I see in Missouri that Waste Water Management is supervised from the State level . . . . here's a link to their Regulations with which you may want to familiarize yourself:

Laws, Regulations & Manuals | Onsite Wastewater Treatment | Health & Senior Services
 

Last edited by Vermont; 10-27-16 at 02:42 PM. Reason: grammar
  #7  
Old 10-27-16, 01:56 PM
S
Member
Thread Starter
Join Date: Oct 2016
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
The black water tank is roughly 40 gallon, probably another 40 gallons of grey water, assuming both tanks were full. I guess that would be worse case. I'm not sure how to use that information to size the leach field though.
 
  #8  
Old 10-27-16, 01:59 PM
S
Member
Thread Starter
Join Date: Oct 2016
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
The area is not along a property line. The entire parcel is 22 acres and the leach field area is at least a couple of acres within the property lines, bordered on one side by a hwy and the downhill side by a pasture.

Thanks for the link. I'll look into that.
 
  #9  
Old 11-15-16, 10:24 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,106
Received 81 Votes on 75 Posts
A septic tank is supposed to rest at about 85% full. Properly, both the inlet and outlet pipes are quite near the top of the tank. Then, normally, for each additional gallon of wast water coming in, a gallon exits for the leach field. There are supposed to be baffles or similar components in the tank so that solid matter settles to the bottom and grease does not migrate to the exit.

The tank would not fit the description of septic tank if the outlet is near or at the bottom of the tank.

The perforated pipe exiting the tank is the leach field pipe. To maximize the life of the leach field, usually the exit pipe branches into several parallel (perforated) pipes and the outlet water is reasonably balanced among them.

The leach field is sized for the expected amount of incoming liquid which in turn is often computed using the number of bedrooms in the house.

A forty gallon tank is probably too small to take any significant amount of inflow (including from a shower or a washing machine) without stirring up solid matter causing the latter to exit and clog (excessively impregnate) the leach field. Also, if the remaining air space in the septic tank plus the remaining air space in the leach lines got completely filled, the drains would back up in the house.
 

Last edited by AllanJ; 11-15-16 at 10:42 AM.
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: